2024-05-06Firstly, perform a jog test, for example, on the software, jog a distance of 10mm to check if the actual movement distance is 10mm, ensuring that the parameter settings match the actual hardware. Then perform the following calibration: when the cutting head is close to the metal plate, the capacitance value on the panel will increase (the C value in the bottom left corner of the HMI homepage); When away from the metal plate, the capacitance value will decrease. Then move the cutting head to the middle position of the stroke for servo calibration, and then move the cutting head close to the metal material for capacitance calibration. Finally, remember to click the OK button to save.